Mike67
Well-Known Member
You need to know the size to properly size your breaker. Also you need to take into consideration voltage drop...which increases with distance. If your over 150' you may need to derate.
Yea its around 15 ft from house to 1st garage around 30 ft from 1st garage to 2nd. The wire that's already under ground will not fit 50 or 60 amp breakers at least the ones I found That's why I need to use a 100 amp breakerYou need to know the size to properly size your breaker. Also you need to take into consideration voltage drop...which increases with distance. If your over 150' you may need to derate.
The wire is already under ground & the newer style panel boxes are already in place. Just trying to use what is there.You can put in a box at each end and reduce the wire size down to what your breaker size is.
There is no problem code wise having wire that is larger than the breaker size in the middle of a run.
But you do need to be careful with connections for aluminum & copper.
Voltage drop is not an issue at these distances.
Like I said earlier you need to determine the size of the wire to correctly size your breaker. The wire is sized to the load carried, the breaker protects the wire. If the wire is larger than the load that's perfectly fine, if the breaker is larger than what the wire can safely carry. That's no bueno and a fire hazard.Yea its around 15 ft from house to 1st garage around 30 ft from 1st garage to 2nd. The wire that's already under ground will not fit 50 or 60 amp breakers at least the ones I found That's why I need to use a 100 amp breaker
The house was built in the 50s not sure when they rain the under ground wires. The 3 wire coming from the house to the first garage is the same type of wire going from the first garage to the second garage.1. It sounds like you have interior wiring buried in the ground, 3 wire cable. You also have a bare neutral. And you should have a 4 wire for each feeder. Although there is an exception in NEC for a existing 3 wire feeder. You need to ground the neutral bar to the panel add the 2 ground rods at each building and land the grounding electrode wire to it on the neutral bar. Also you do not need main disconnects in the feeder panels if you have six or less disconnecting breakers in each. So if you have main lug panels no need to add mains. So your 1st feeder disconnect, will be in the house panel. Feed the main lugs in the first building then you will add a breaker in that panel that meets the wire size and load to the second building. Again no main needed on either if less than 6 disconnecting breakers. Also all new 120 volt outlet shall be GFCI protected if they are in a garage.
The solid copper wire is going to a ground rod. I have to install a second one. Didn't know I needed 2. I would replace the 100 amp breaker with a 50 or 60 breaker but the wire is to big & will not fit into them. I don't want to dig up that wire if I don't have to.This should work but not code compliant. Your panels are probably not listed to have 100 amp breakers in the the lower section, it would be on the label on the side of the panel. I would suggest lowering it to a 50 amp. Also I would wrap black electric tape and cover your neutral conductor except were the connection is made. And I do not see we’re the neutral bar is grounded (connected) to the panel. I see a hole in the upper right corner of the neutral we’re a bond screw would fit and screw to the back of the panel to make a connection. Or you can add a “L” shape lug with a bolt and nut on the panel and run a wire jumper to the neutral bar.
Most people who are not in the trade don't understand the difference.With AC power nothing is ever wired in series.
Exactly, and it's not learned in an afternoon.Just remember, electricity is not a hobby.............